ways of producing 3 phase ac from single phase:
1)a motor-generator set (m-g set) where a single phase motor drives a 3
phase generator which is bulky, expensive & complex
2)electronic inverters using power igbts or mosfets controlled by
processors which produces the "ideal" 3-phase but is very expensive and
more comlpex.
3)Static converters that use a transformer to produce 2 phases from one,
and at the required voltage, plus a capacitor to produce a third phase when
a load motor is connected. Such a converter is cheap to manufacture but has
four serious disadvantages:
a) the load must be a motor and it must be known in advance if it is star
or delta connected
b) if the load has more than one motor then the highest power motor must
always be switched on first
c) the load motor will only run at 70% of normal torque
d) there is a minimum power limit as well as a maximum so the capacitor
value must be manually switched to match the load.
4)Rotary converters add an unloaded motor-generator to the static
converter, eliminating problems a) to d). The motor-generator can be
considered as analogous to the flywheel of an internal combustion engine;
it smooths the flow of power and maintains the equal time relationship
between the three phases. Efficiency is much higher than for an inverter
solution, reaching 95% for most of the power range.
basic rotary converter: Tesla polyphase induction motors
modified with magnetic contactors & relays:
pb=push-button switch (start=green, stop=red)
k1=k4=20-50A 220vac magnetic contactor (150% of motor FLA rating; limit under 10hp)
k2=k3=5A 220vac relay
t1=220v 0-30 sec timer relay
olr=overload relay set @ 2-3 sec; starting time depends on the motor size
c1=c2=12-16uf per motor's hp
c3=50-100uf per motor's hp
l=220v pilot lamps
m=1-10hp 220v 3-ph induction motor
1)a motor-generator set (m-g set) where a single phase motor drives a 3
phase generator which is bulky, expensive & complex
2)electronic inverters using power igbts or mosfets controlled by
processors which produces the "ideal" 3-phase but is very expensive and
more comlpex.
3)Static converters that use a transformer to produce 2 phases from one,
and at the required voltage, plus a capacitor to produce a third phase when
a load motor is connected. Such a converter is cheap to manufacture but has
four serious disadvantages:
a) the load must be a motor and it must be known in advance if it is star
or delta connected
b) if the load has more than one motor then the highest power motor must
always be switched on first
c) the load motor will only run at 70% of normal torque
d) there is a minimum power limit as well as a maximum so the capacitor
value must be manually switched to match the load.
4)Rotary converters add an unloaded motor-generator to the static
converter, eliminating problems a) to d). The motor-generator can be
considered as analogous to the flywheel of an internal combustion engine;
it smooths the flow of power and maintains the equal time relationship
between the three phases. Efficiency is much higher than for an inverter
solution, reaching 95% for most of the power range.
basic rotary converter: Tesla polyphase induction motors
modified with magnetic contactors & relays:
pb=push-button switch (start=green, stop=red)
k1=k4=20-50A 220vac magnetic contactor (150% of motor FLA rating; limit under 10hp)
k2=k3=5A 220vac relay
t1=220v 0-30 sec timer relay
olr=overload relay set @ 2-3 sec; starting time depends on the motor size
c1=c2=12-16uf per motor's hp
c3=50-100uf per motor's hp
l=220v pilot lamps
m=1-10hp 220v 3-ph induction motor
longthrow- AAA Battery
- Posts : 37
Join date : 2012-01-10
Age : 44
Location : cebu
Re: single phase to 3-phase converter
wow galing. +1 po kayo
Digitap- Admin
- Posts : 927
Join date : 2010-09-03
Age : 33
Location : Makati City
Re: single phase to 3-phase converter
longthrow wrote:
t1=220v 0-30 sec timer relay
olr=overload relay set @ 2-3 sec; starting time depends on the motor size
error sa typing! correction:
t1=220v 0-30 sec timer relay, set @ 2-3 sec; starting time depends on the motor size
olr=overload relay set @ motor's fla (full-load amps)
@mayalin: thanks!
longthrow- AAA Battery
- Posts : 37
Join date : 2012-01-10
Age : 44
Location : cebu
Re: single phase to 3-phase converter
plus one point sayo sir
volter- Admin
- Posts : 176
Join date : 2010-08-24
Age : 47
Re: single phase to 3-phase converter
+1 syo din sir..marmi ako matutunan dito..tambay lang muna.
jojogreg- AAA Battery
- Posts : 43
Join date : 2012-10-03
Re: single phase to 3-phase converter
longthrow wrote:ways of producing 3 phase ac from single phase:
1)a motor-generator set (m-g set) where a single phase motor drives a 3
phase generator which is bulky, expensive & complex
2)electronic inverters using power igbts or mosfets controlled by
processors which produces the "ideal" 3-phase but is very expensive and
more comlpex.
3)Static converters that use a transformer to produce 2 phases from one,
and at the required voltage, plus a capacitor to produce a third phase when
a load motor is connected. Such a converter is cheap to manufacture but has
four serious disadvantages:
a) the load must be a motor and it must be known in advance if it is star
or delta connected
b) if the load has more than one motor then the highest power motor must
always be switched on first
c) the load motor will only run at 70% of normal torque
d) there is a minimum power limit as well as a maximum so the capacitor
value must be manually switched to match the load.
4)Rotary converters add an unloaded motor-generator to the static
converter, eliminating problems a) to d). The motor-generator can be
considered as analogous to the flywheel of an internal combustion engine;
it smooths the flow of power and maintains the equal time relationship
between the three phases. Efficiency is much higher than for an inverter
solution, reaching 95% for most of the power range.
basic rotary converter: Tesla polyphase induction motors
modified with magnetic contactors & relays:
pb=push-button switch (start=green, stop=red)
k1=k4=20-50A 220vac magnetic contactor (150% of motor FLA rating; limit under 10hp)
k2=k3=5A 220vac relay
t1=220v 0-30 sec timer relay
olr=overload relay set @ 2-3 sec; starting time depends on the motor size
c1=c2=12-16uf per motor's hp
c3=50-100uf per motor's hp
l=220v pilot lamps
m=1-10hp 220v 3-ph induction motor
okis to...
DJFEL- 24V BATTERY
- Posts : 1780
Join date : 2012-11-21
Age : 42
Location : SIUIJOR
Re: single phase to 3-phase converter
Ngayon ko lang nabasa ito. Meron pa kayang follow up?
james- 24V BATTERY
- Posts : 1081
Join date : 2011-11-14
Re: single phase to 3-phase converter
sir longthrow, pwedi ba ma klaro ko yong control circuit mo,medyo potol,tanong kulang sir gagana ba ang electronic phase sequencer(under voltage,lower voltage protection relay)1phase to 3 phase?thanks
daltanics- AA Battery
- Posts : 118
Join date : 2011-10-30
Age : 44
Location : davao city
Re: single phase to 3-phase converter
sir daltanics,
meron kaba clearer pic or model ng protection relay?
meron kasi pang single phase na relay, meron din pang 3ph.
if you are using 3ph relay into single ph operation, naka protect na kaagad yan kc absent ang 2 phases (no phase voltage).
hidi yan putol sir, that is converting a single phase line into 3 phase utilizing a 3ph motor into a 3ph generator aka rotary converter.
meron kaba clearer pic or model ng protection relay?
meron kasi pang single phase na relay, meron din pang 3ph.
if you are using 3ph relay into single ph operation, naka protect na kaagad yan kc absent ang 2 phases (no phase voltage).
hidi yan putol sir, that is converting a single phase line into 3 phase utilizing a 3ph motor into a 3ph generator aka rotary converter.
longthrow- AAA Battery
- Posts : 37
Join date : 2012-01-10
Age : 44
Location : cebu
daltanics- AA Battery
- Posts : 118
Join date : 2011-10-30
Age : 44
Location : davao city
Re: single phase to 3-phase converter
ok sir longthrow,ito kadalasan genagamit sa mga control ng sub. pump dito sa riyadh.
daltanics- AA Battery
- Posts : 118
Join date : 2011-10-30
Age : 44
Location : davao city
Re: single phase to 3-phase converter
phase monitor, over & under voltage protection relay pala yan sir.
'yan hawak nyo ay pang 3ph na variant, as indicated sa label (3ph/380v) , pero meron din naman pang 1ph na ganyang relay sir.
eto specs nyan sir:
http://www.jyhkuen.com.tw/monitor/ejvm.pdf
similar relay pang 1ph:
http://store.acradiosupplyinc.com/nter67-11a10-120relay-vltgmonitor120vac.aspx
'yan hawak nyo ay pang 3ph na variant, as indicated sa label (3ph/380v) , pero meron din naman pang 1ph na ganyang relay sir.
eto specs nyan sir:
http://www.jyhkuen.com.tw/monitor/ejvm.pdf
similar relay pang 1ph:
http://store.acradiosupplyinc.com/nter67-11a10-120relay-vltgmonitor120vac.aspx
longthrow- AAA Battery
- Posts : 37
Join date : 2012-01-10
Age : 44
Location : cebu
Re: single phase to 3-phase converter
aus ha thnx sa information
Xyphro- AAA Battery
- Posts : 1
Join date : 2014-05-26
Age : 35
Location : Davao
Similar topics
» DC to DC converter
» RENCO TV CONVERTER.
» 12V to +/- 30V DC to DC Converter smps
» Laptop/PC to TV Converter (VGA connectors)
» RENCO TV/CABLE CONVERTER (EEPROM Dumps)
» RENCO TV CONVERTER.
» 12V to +/- 30V DC to DC Converter smps
» Laptop/PC to TV Converter (VGA connectors)
» RENCO TV/CABLE CONVERTER (EEPROM Dumps)
Page 1 of 1
Permissions in this forum:
You cannot reply to topics in this forum
|
|